Discussion Starter · #1 ·
I have a 40 ton AAON rooftop unit with copeland scroll compressors running on 410a refrigerant. I was wondering what my SH and SC should be. I have 132 psi suction and 350 psi discharge and am getting a 26 deg superheat and a 61 deg subcool. It has a TXV. My outdoor temp is 80 deg and return air temp of 72. I dont really have much experience with 410 and not sure what kind of numbers i should be getting. Thanks for any help.
 

·
Registered
Joined
·
33 Posts
I have no experience with 40 ton equipment, but superheat and subcooling values are generally consistent regardless of the type refrigerant. Which would suggest 26 is high for the superheat and 61 is way high for the subcooling.

The suction pressure and SST is normal, but 350 could be high for the head depending on the unit SEER. Residential 13 SEER equipment would be closer to 300 for an 80 degree ambient. It's about right for 10 SEER.

Are you using the right P-T chart for saturated temperatures?
 

·
Registered
Joined
·
33 Posts
Something else to consider...to have 61 F subcooling with that head pressure, the liquid line would have to be 45 F or so. That sound right?
 

·
Registered
Joined
·
2 Posts
Discussion Starter · #4 ·
I am using the temp reading on my guages. They are set up for 410 refrig. I am getting a 45 deg sat. temp on the low side and reading 76-77 on the line itself at the compressor.
 

·
Registered
Joined
·
33 Posts
I am using the temp reading on my guages. They are set up for 410 refrig. I am getting a 45 deg sat. temp on the low side and reading 76-77 on the line itself at the compressor.
Well, that eliminates errors in saturated temps. But I still can't fathom a 60 degree subcooling value. I once saw a resi heat pump in the heat cycle with 50 F subcooling, which way the hey overcharged...:blink::001_tongue:
 

·
Registered
Joined
·
1 Posts
Need more info. Does your unit have 2 twenty ton compressor or 4 ten ton. does it have a mod reheat. unit model # will help. I work on Aaon units about every day and may be of some help
 

·
Registered
Joined
·
15 Posts
At those pressures and sat. vap. temps I dont see how you could have 61sc. Are you sure on the sc reading. Measure the temperature of your liquid line and convert the 350 to temperature on the pt chart, not on your gauges. Subtract your liquid lie temp from your pt conversion temp, and you will have sc reading. :thumbsup:
 

·
Banned
Joined
·
67 Posts
Superheat and subcooling readings must be taken when the system is in a steady state condition. typically a residential system will be at steady state after ~10-15 minutes, but can be longer..
 