Summary: Lennox G24M furnace. Normal startup sequence, but 5-20 seconds after flames start, the gas shuts off. This cycle repeats. It is NOT the flame sensor (more below).
Flame sensor is fine based on testing using micro-ampere meter. (I cleaned it anyway.) Other tests (see below) completely rules out the flame sensor.
I measured the voltage across the pressure switch. I get 24 VAC just after the inducer motor starts, then 3-5 seconds later, after inducer gets to full speed, that goes 0 VAC indicating the pressure switch has closed.
So, all normal so far in the startup sequence.
However, 5-20 seconds after the flames start, the flames stop and, simultaneously, the voltage across the pressure switch goes from 0 to 24 VAC indicating the switch has opened. After 2-3 seconds, with the inducer motor still running, the pressure switch closes again, and after the 40 second purge, the furnace ignites, runs for a few seconds, and then shuts down. The blower starts shortly after the first cycle and continues to run after that, so I have both the inducer fan and the furnace fan running.
I get no error codes.
To make sure it is the pressure switch which is causing the furnace to shut down, I bypassed the pressure switch (shorting across the leads) just after it had closed. When I did this the furnace stayed lit and ran until I removed the jumper wire. It then instantly shut down. Therefore, it is not the flame sensor.
The flames are being sucked into the furnace, as they should be. Neither rollout switch is being activated, and the high temp switch did not open during any of these cycles (I tested these).
The key to the whole thing is why does the pressure change only after the flames start? I would think that a plugged exhaust vent or cracked heat exchanger would cause the pressure switch to stay open during the cold air purge and the furnace would not start at all.
I bought and installed a new 0.40" pressure switch. The old one was spec'd at 0.46". After installation of the new pressure switch, the furnace ran for 20-30 seconds instead of 4-10 seconds.
But now it gets interesting.
I let the furnace short cycle for half a dozen cycles and each time it ran a little longer, and eventually I was getting over two minutes of operation per cycle.
I was unable to get to the vent on the roof of the two-story house and was unable to disassemble the metal vent underneath the cap. This is the upstairs furnace and it is in the attic. It was installed in early 1995 but everything today looks as new as the day it was installed. The burners and the burner orifices are pristine as is all the sheet metal. The length of the flu from the furnace to the roof vent is less than eight feet total.
The only thing I can think of is that there is something in the roof vent or in the heat exchanger that built up during the seven months the furnace isn't used (we don't need heat here from April until late November). However, that doesn't make sense to me because if there was a blockage, the pressure switch should never close and the furnace should never start in the first place.
So here's the $64,000 question (reference to quiz show that was popular when I grew up in the 1950s): What would cause the pressure to significantly change only a few seconds after the furnace starts heating?
Any ideas would be greatly appreciated.
Thanks!
Flame sensor is fine based on testing using micro-ampere meter. (I cleaned it anyway.) Other tests (see below) completely rules out the flame sensor.
I measured the voltage across the pressure switch. I get 24 VAC just after the inducer motor starts, then 3-5 seconds later, after inducer gets to full speed, that goes 0 VAC indicating the pressure switch has closed.
So, all normal so far in the startup sequence.
However, 5-20 seconds after the flames start, the flames stop and, simultaneously, the voltage across the pressure switch goes from 0 to 24 VAC indicating the switch has opened. After 2-3 seconds, with the inducer motor still running, the pressure switch closes again, and after the 40 second purge, the furnace ignites, runs for a few seconds, and then shuts down. The blower starts shortly after the first cycle and continues to run after that, so I have both the inducer fan and the furnace fan running.
I get no error codes.
To make sure it is the pressure switch which is causing the furnace to shut down, I bypassed the pressure switch (shorting across the leads) just after it had closed. When I did this the furnace stayed lit and ran until I removed the jumper wire. It then instantly shut down. Therefore, it is not the flame sensor.
The flames are being sucked into the furnace, as they should be. Neither rollout switch is being activated, and the high temp switch did not open during any of these cycles (I tested these).
The key to the whole thing is why does the pressure change only after the flames start? I would think that a plugged exhaust vent or cracked heat exchanger would cause the pressure switch to stay open during the cold air purge and the furnace would not start at all.
I bought and installed a new 0.40" pressure switch. The old one was spec'd at 0.46". After installation of the new pressure switch, the furnace ran for 20-30 seconds instead of 4-10 seconds.
But now it gets interesting.
I let the furnace short cycle for half a dozen cycles and each time it ran a little longer, and eventually I was getting over two minutes of operation per cycle.
I was unable to get to the vent on the roof of the two-story house and was unable to disassemble the metal vent underneath the cap. This is the upstairs furnace and it is in the attic. It was installed in early 1995 but everything today looks as new as the day it was installed. The burners and the burner orifices are pristine as is all the sheet metal. The length of the flu from the furnace to the roof vent is less than eight feet total.
The only thing I can think of is that there is something in the roof vent or in the heat exchanger that built up during the seven months the furnace isn't used (we don't need heat here from April until late November). However, that doesn't make sense to me because if there was a blockage, the pressure switch should never close and the furnace should never start in the first place.
So here's the $64,000 question (reference to quiz show that was popular when I grew up in the 1950s): What would cause the pressure to significantly change only a few seconds after the furnace starts heating?
Any ideas would be greatly appreciated.
Thanks!