Trane water source heat pumps
Old 01-13-2011, 05:47 PM   #1
Lash5adam's Avatar
Trade: Service and duct
Have a system with about 20 water source heat pumps on it and 2 of them are acting up. The 2 that are acting up are working fine in cooling and compressor cuts out in heating. One of the units was low on refrigerant. I reclaimed the system, checked for leaks, and weighed refrigerant back in. It ran fine until it was satisfied. Then it started cutting the compressor out on heat again. Some times it would cut out after 6 seconds and if I put it in cooling then back to heat it would run for at least 3 min. Any Ideas.
Lash5adam is offline
Old 01-14-2011, 10:08 AM   #2
linebacker's Avatar
Trade: Air condition sales & service
Re: Trane water source heat pumps
Are you checking pressures and amps. when it is running and see what is cutting out?
linebacker is offline
Old 01-14-2011, 03:14 PM   #3
Lash5adam's Avatar
Yes amps are good compressor is cutting out on high head pressure.
Old 01-14-2011, 03:15 PM   #4
Lash5adam's Avatar
Also checked air flow and cleaned coil. Air flow is good.
Old 01-14-2011, 03:29 PM   #5
linebacker's Avatar
I'm not a tech, but we have installed alot of WHP's over the years. It's sounds like you are checking the right things. To run the pressures up that fast would seem to be a restriction in the freon side, maybe close to the reversing valve. There may be a strainer in the line that will stop up in one direction. If you have high pressure and pulling down on the low pressure side, you have a restriction. Good luck.
Old 01-14-2011, 03:39 PM   #6
Lash5adam's Avatar
Already tried the reversing valve. It didnt make a difference now I think its the TXV. I don't know what else it could be.
Old 01-17-2011, 09:38 AM   #7
linebacker's Avatar
There may be a strainer in the area around the heat txv. If you can, let me know what the fix ended up being. I still believe you are on the right track.
Old 01-17-2011, 04:13 PM   #8
Lash5adam's Avatar
will let you know what the fix is. Wont be working on it again for a week or so. It is not as important as other jobs.
Old 01-25-2011, 08:02 AM   #9
HintonAC-LeoTav2's Avatar
Trade: Heating and Air Conditioning Service and Installation Tech
I ran into a similar problem late last year with an air cooled Heat Pump. I'd check for a temp drop across the lines of the heating liquid line dryer and the TXV. You may find your rescriction in there.
HintonAC-LeoTav2 is offline
Old 01-26-2011, 05:42 AM   #10
Lash5adam's Avatar
I changed the txv valve and filter dryer all is good now. Thanks
Old 01-26-2011, 09:04 AM   #11
linebacker's Avatar
You the man!
Old 04-17-2011, 05:27 PM   #12
siddle's Avatar
Trade: HVAC Service, Roofing contractor
Had a similar problem with our Trane water source heat pump. Thanks to all of you for your valuable tips. We were able to fix that. And a big thank you to Lash5adam.
Absolute Steel— Steel building and carport kits with nationwide jobsite delivery. Easy DIY—America’s easiest to install building system. Watch the video & see for yourself.
siddle is offline
Old 05-18-2011, 01:05 PM   #13
ironpit's Avatar
Trade: hvac contractor
One of the dealers I help takes out the strainers on every txv. I tell him it is best to leave them in. He has been doing hvac for almost forty years and says it is better to take the strainers out. I still disagree. I try to always side with manufacturer design. Does anyone else, with experience, take these out?
ironpit is offline
Old 10-03-2011, 02:14 AM   #14
NRG$WIZ's Avatar
Trade: Commercial Building Engineer 8 years/multihousing 11 years/EPA universal
Is the reversing valve working/how about the cut outs /any oil-any leaks found-sometimes the leak is in the water side.
NRG$WIZ is offline
Good Source For Technicians acme Business, Marketing, and Sales 23 09-06-2011 12:28 PM
tankless water heaters OZIE55 Residential HVAC Forum 1 10-24-2010 07:48 AM
under water airconditioner lol supertek65 HVAC Pictures 4 10-24-2009 04:59 PM
Acadia heat pumps RoBoTeq HVAC Material and Products 2 09-12-2009 08:26 AM