Trade: service tech
R410A to R-22
Other than pressure switch settings and oil charge, is there any reason you can not use R-22 in R410A condensing unit with R-22 evap coils? 25 ton coils are expensive to change unless totally NECESSARY. Manufacturers are using the CYA argument. Is it legitimate? Thanks
Trade: Supermarket Refrigeration
Re: R410A to R-22
Since there is a HUGE difference in capacity between the two refrigerants, I'm going to say that it won't work well.
The oil would be a non-issue as POE is compatible with all types of refrigerant, that isn't an issue. |
Trade: Replacement Coils
Re: R410A to R-22
I think there is a potential issue with rubber seal deterioration as well.
Trade: HVAC Service, Roofing contractor
Re: R410A to R-22
Many contractors are experiencing compressor burnout problems with R-410A HVACR systems soon after they're converted from R-22 refrigerant.
Absolute Steel— Steel building and carport kits with nationwide jobsite delivery. Easy DIY—America’s easiest to install building system. Watch the video & see for yourself. |
#5 | |
Re: R410A to R-22Quote:
Then they aren't doing something right.
Trade: heating,cooling,refrigeration
Re: R410A to R-22
i would say that the condensing coil would be different in the capacity and if you are using the same compressor there might or there is a difference in the pumping ratio in the compressors but i could be wrong on this.
Re: R410A to R-22
BTU for BTU, an R22 compressor moves more refrigerant then an R410A compressor. So using R22 in a R410A condenser, will lower its capacity.
Re: R410A to R-22
What do you think the problem may be? Any ideas?
Re: R410A to R-22
Some possible causes.
Didn't blow out the line set if they reused it, and left too much min oil in the system. Reused old indoor coil and didn't blow it out, or its mismatched to the condenser. Didn't pull a low enough vacuum, which left too much moisture in the system. Poor brazing technique. Causing leak problems and running system in a vacuum drawing air and moisture into the system, then pumping the remaining charge into the condenser when to fix the leak, which means only pulling a vacuum on the line set and coil, leaving moisture in the charge that has been pumped back into the condenser, causing an acid burn out later. Often, the LLFD isn't changed when the leak is at a braze joint outside of the condenser. A few minutes saved along with a few dollars for the LLFD that wold ahve to be replaced under warranty. And you end up a problem that is wrongfully blamed on R410A.
Re: R410A to R-22
Thank you so much. Lemme check whether it works or not. I'll let you know soon.
Trade: Brad
Re: R410A to R-22
R410a requires much less compressor horsepower per ton then R22 due to running with a higher compression ratio .So running R22 in a R410a compressor could cause over amping even with a low head and high suction potential High superheat and ultimately burn the compressor another problem may be oil return. Would not recommend this practice. If it was meant to run on R22 , R407C Etc it would have a alternate rating on it.
#12 | |
Trade: David Roberts
Re: R410A to R-22
Volumetric compression will not allow the use of a 410A compressor with r22. don't waste your time or money.
Re: R410A to R-22
Beenthere said:
Didn't pull a low enough vacuum, which left too much moisture in the system. Amen to that!! |