Trade: service manager
icm325 electronic fan speed control
Can ICM325 be used to control head pressure if the system does not have a txv ? Why would this be if we are just slowing condenser fan motor during low ambient temperature ? Application is r22 2.5 ton split system with old Carrier air handler , has orifice. Any input would be great.
Re: icm325 electronic fan speed control
I wouldn't do it.
You have more control using a low ambient kit that is based solely on pressure versus airflow. Stick to the tried and true........... |
Not sure what you mean by low ambient kit . If you talking about headmaster type pressure valve this cant be used as there is no receiver on the system. We do not want to use fan cycle switch as condenser fan cycles too rapidly and we we have too much pressure variations with this type of control.
Old Fart !
Trade: Commercial Maintenance/Service Technichian
I'm putting my $.02 worth now
![]() ![]() .... A solid state low ambient kit that modulates the RPM of the OFM by reacting to the temperature of the liquid line (sensor part of kit) should work just fine for this application.... About $150. (wholesale) |
#5 | |
Re: icm325 electronic fan speed controlQuote:
This area reflects the indoor load. And allows the control to have a tighter rain on the OFM's speed. On fixed metering device systems. You can have a lot of flash gas, since its only feed control is by the pressure difference between the liquid line and the evap coil. You can often run less then 100 PSIG difference. And end up starving the coil, and freezing it up anyway. If this is for a electronic or mechanical area. raise your indoor air flow also. It will also help keep the coil from freezing/frosting just before the control slows the blower on start up.
| The Variable Speed Blower | beenthere | General HVAC Discussion | 20 | 12-21-2011 04:06 PM |
| DDC Control for the mid market | jwhite | Commercial HVAC Forum | 11 | 08-30-2010 05:28 PM |
| I need an ignition control module | thehvacguy | Residential HVAC Forum | 4 | 03-27-2010 10:35 PM |
| ICM325 electronic fan speed cotrol | sammy | General HVAC Discussion | 3 | 02-15-2010 07:51 AM |
| txv coil temp control? | RoBoTeq | Residential HVAC Forum | 14 | 09-11-2009 12:10 AM |