Expansion valve issues???
Old 03-09-2010, 09:29 PM   #1
Delta31's Avatar
Trade: HVAC Technican
Angry
I'm having issues with a Lennox 7.5ton 410a heatpump split system. This system has a dual evap coil ran by a single circuit compressor. My run pressures are way of at 60 low side and 310 high side, I have checked the lineset and expansion valves for any restrictions and could not find any. I'm not sure if my valves are sized properly, they are both 4ton and were installed during installation. Are these the proper size??
Delta31 is offline
Old 03-10-2010, 02:16 PM   #2
Re: Expansion valve issues???
sounds like it's restricting volume. whats your superheat like? if your total superheat is low i betcha the one valve is starving its coil and then starving the compressor affecting the mass/flow rate. the valves are 4 tons each, if they're both 4 tons, then maybe one is feeding more to the one coil than to the other. check the independent evap outlet for hi superheat at each evap outlet to see if one is starving. i can suggest an EPR to even it out but perhaps splitting up the coils capacity like....3.5 and 3.5 or 3.5 and 4. good luck
Old 03-11-2010, 06:09 AM   #3
As above. Each TXV and its evap coil must be checked independently of the other.
You say its a heat pump. I'm guessing your running it in cooling mode. Are you?
Posting all readings can help us help you.
SH of both TXV's, SC at outdoor unit, and at the TXV's, Indoor and outdoor ambients.
CFM of indoor blower(not its blowing out good).
Temp delta across indoor and outdoor coils.
Old 03-16-2010, 01:22 PM   #4
Well? what happened?
Left hand thread radiator valve. JohnH1 General HVAC Discussion 7 04-16-2011 08:12 AM
TX Valve 101 Yuri General HVAC Discussion 3 07-16-2009 04:39 PM