I need advice of professionals to have answer at questions:
1) How much power (kW) should have heat exchanger to cool down refrigerant on high side?
2) How much water could be heated in 1 hour from 65F to 104 F?
Here is Chiller Wesper WLS 1004 ELN documentation: http://www.wesper.com/fichiers/Site%..._vls_w_6gb.pdf
It has 4 Copeland scroll compressors ZR310KCE, 25HP each compressor.
Documentation of compressor: http://www.elektronika-sa.com.pl/tcm...=4&Tab=2&LID=2
For this project we planed to use two heat exchangers for each circuit (Wesper has two refrigerant circuits, two compressors on each side)
Known parameters:
Assuming that 1 compressor on each circuit will run all time.
Refrigerant: R407c
Refrigerant high side temperature: 150F
Refrigerant boiling temperature: 41 F
Chiller cold water set temperature: 48 F
Considering water temperature entering in heat exchanger (condenser unit): 65 F
Desired water temperature after heat exchanger (condenser unit): 104 F
Any advice will be appreciated.
Thank you
AlexGe is offline
Old 09-08-2013, 06:40 AM   #2
Re: Choose right water condenser for my ciller Wesper WLS 1004 ELN
Roughly 935 gallons an hour, if the compressor is working at full load.
Old 09-10-2013, 04:00 PM   #3
AlexGe's Avatar
Trade: Ungar
Thank you for answer.
Could you be so kind and tell me how you determine that?
From compressor technical data: Displacement [m/h]:71,4
The chiller has TEV model: Danfoss TEZ 55 , it will reduce total flow rate of system.
AlexGe is offline
Old 09-10-2013, 04:14 PM   #4
25 HP equals 300,000 BTUs.
Desired water temp of 104F minus entering water temp of 65F equals 39F delta.
1 BTU to raise or lower 1 pound of water 1F
300,000 divided by 39 equals 7,692 pounds of water heated to 104F.
7,692 divided by 8.22(pounds of water per gallon) equals 935 gallons of water an hour.
I probably should have used 8.33 pounds per gallon(since the entering water temp is 65). That changes the answer to 923 gallons an hour.
Need ultra low profile condenser Jeffrey Jay Commercial HVAC Forum 6 04-11-2016 09:40 PM
R410a acoil and R22 condenser nooche General HVAC Discussion 1 08-18-2013 07:11 AM
Ants in Condenser? ThunderCow Residential HVAC Forum 42 01-11-2011 04:32 AM
Freon trapped in condenser blazer sheetmetal Residential HVAC Forum 7 05-15-2010 03:37 PM
Condenser coils going bad DCHVAC Residential HVAC Forum 40 07-10-2009 10:22 PM