Why does water vapor drip back down a vent pipe.
Old 03-15-2009, 01:51 PM   #1
pcplumber's Avatar
What causes the water to drip down a vent pipe on a forced air furnace? We installed many furnaces and water dripped back down the pipes and literally destroyed several furnaces. I am curious about the physical or chemical reaction that causes the problem.
pcplumber is offline
Old 03-22-2009, 02:17 PM   #2
NHMaster3015's Avatar
Re: Why does water vapor drip back down a vent pipe.
Flue gasses condensing in the flue. for non condensing appliances the flue gas must be above 400 degrees. Long flue runs will also cool the gasses and cause the problem.
NHMaster3015 is offline
Old 03-22-2009, 04:05 PM   #3
pcplumber's Avatar
When we replace an existing FAU, and connect with single wall pipe, and connect to a transite pipe, water will pour backwards into the furnace and flood the controls. Often, there is an oily substance that comes down the pipe. At one time I thought the customer stored a can of motor oil on the furnace and the can leaked. It looked exactly like 3-in-1 oil. Most people think their roof jack is leaking, but these leaks occur when we haven't had rain in over a leak.
The furnace instructions require us to install double wall metal pipe from the outlet of the furnace through the roof.
Old 03-22-2009, 09:55 PM   #4
not no junior member
uaplumber's Avatar
Trade: Owner Plumbing/Heating shop
Size your venting properly. Too large and you won't get a proper "stack effect", the gasses will cool off and condensate inside the vent. End result? New Furnace.
uaplumber is offline
Old 03-24-2009, 11:34 PM   #5
pcplumber's Avatar
I'll have to read those instructions again.
Old 05-17-2009, 09:57 AM   #6
I'd check with the mfg about what the flue temp should be. 400 degrees seems off to me for some reason. It's possible that the fan speed is too high;that would allow more heat in the house then goes up the chimney.
Are you using chimney liner kits? The HO keeping the the temp low in the home would also cause stack to fall below dew point of burnt fuel.
Another thing is over sized duct work will contribute to this problem
Old 05-28-2009, 08:52 PM   #7
Yuri's Avatar
Oily substance? Are you venting into an unlined masonry chimney that was previously used for oil. In my area the venting of the furnace needs to match the chimney liner and the liner has to be accurately sized for the firing rate of the furnace and water heater. We use B venting or a smaller single liner inside a existing larger one sometimes.
Yuri is offline
Old 05-28-2009, 09:04 PM   #8
Administrator
Nathan's Avatar
Trade: Administrator
Welcome to the site Yuri... glad your here.
Nathan is offline
Old 05-29-2009, 10:51 PM   #9
scooter's Avatar
pcplumber
can you give the exact set up of these furnaces.
it sounds like there has been more then one, but are they in different houses or all in the same house.
What furnace came out, what went in.
Chimney configuration.
Use brand names and models #'s whenever you can.
scooter is offline
Old 05-30-2009, 09:51 AM   #10
The flue tmep is defiantly the issue here. If it's an 80% furnace with out a metal chimney liner you will get condensation in that oily form you describe.
I had it happen to me as a rookie. I called the local utility and was informed that is was some type of additive put into the gas along the transmission rout .
To burn it off the flue temp must be at optimum temp.
I think you are due for a combustion analysis. If you don't have the equipment then hire an hvac friend to do it for you. You will get a wealth of knowledge from it.
Old 05-30-2009, 04:05 PM   #11
Get a copy of the GAMA vent tables. Plus a copy of the IGFC.
It will have vent size tables.
As others have said. It sounds like your flue gas is cooling too much as it goes up the flue.
Oversize flues/chimneys cause much of this.
While not as often. If you install a properly sized furnace in a house that had amplely sized duct work. Its also posible to have too much air moving across the heat exchanger. And also cool the flue gasses too much.
When ever possible. If you can find an extra install manual for a furnace, weather the brand you install or not. Grab it, and keep it.
The install instructions for one, are not always the same as the next brand.
Old 06-05-2009, 10:56 PM   #12
hector's Avatar
Trade: hvac tech
This is the reason we aren't allowed to vent back into transite....Some manufactures also advise venting into transite.. When I run into transite . I line it with DW vent.. If it's oval transite.. I install a 90+ furnace
hector is offline
Old 06-05-2009, 11:26 PM   #13
I probably know it by another name, but what is transite?
Old 06-09-2009, 01:44 AM   #14
hvactech's Avatar
Trade: commercial/residential HVAC service/installation 20+years
Send a message via AIM to hvactech Send a message via Yahoo to hvactech
Yeah what is Transite?
hvactech is offline
Old 06-09-2009, 07:23 AM   #15
http://www.inspect-ny.com/sickhouse/asbestoslook7.htm
Old 06-09-2009, 10:43 AM   #16
http://mail.google.com/mail/?ui=2&ik...2&disp=attd&zw
Old 06-09-2009, 04:40 PM   #17
munshin's Avatar
Trade: hvac apprentice
Out here in De. we are allowed to use Pvc for the High 90% over above. I am gathering that is the type of heater in use. If that is the case, then, there sounds like you have a pitch pblm.
munshin is offline
Old 06-09-2009, 06:15 PM   #18
No its not a 90% furnace as any body in the HVAC industry can plainly tell from the posts.
Are you employed in the hvac business or just a civilian dabbler?More
Old 06-09-2009, 06:51 PM   #19
Administrator
Nathan's Avatar
Sounds like he's just getting started so we will see. Apprentices are welcome on the site as with anyone who works full time in the industry. I'll post more about who is who is not allowed soon.
Thanks.
Nathan is offline
Old 06-09-2009, 07:12 PM   #20
lol...right on it, ey, Boss