Trade: service tech
normal suction low head pressure
im in the field 3 years now and this is the first time ive come across this. residential split system 1.5 tons and i had a good suction pressure but my head pressure was super low, only 150-160. the strange thing is operations seemed pretty normal. cold suction line, warm liquid line, condenser was putting out good heat, good indoor air flow, clean filter clean coils. compressor is brand new. any feedback would be greatly appreciated as i am at a loss on this one.
Re: normal suction low head pressure
good suction pressure...How good?
![]() cold suction line...How cold? ![]() warm liquid line...How warm? ![]() What was the outdoor temp and indoor temp? ![]() I'll take a guess...the orifice is over sized and the system is undercharged. |
Trade: service tech
69 suction press, not ice cold but sweating
liquid line, a little warm but by not means hot 82-85F outside 70-72F inside unit was changed a year ago before i was with the company, he sent me back to do the compressor on warranty. smelled like a pretty bad burn out. |
#4 | |
Re: normal suction low head pressureQuote:
Assuming the system is 10 SEER/fixed metering and estimating the indoor wetbulb at 60F: With those temps, target superheat would be very low, just a few degrees, so the suction line temp would be close to the saturated suction temperature (40F)...truly "beer can cold". ![]() Estimated condensing temps would be 20 above the outdoor temp, or 105F with a saturated pressure at 210psi. I would still guess the system is undercharged. The liquid line feels "warm" because of low subcooling. The orifice size isn't necessarily in question. |
Trade: Journeyman Service Tech resi/light commercial
No offense, but you need to go back over basic charging procedures to have any clue if a unit is charged correctly. Superheat, subcooling, outdoor ambient and temp drop across evap. as a minimum.
Double check your calibration on you gauges that could also be an issue.
Is there a strainer in the liquid line? it may be partially plugged from the burn out.
Is their a strainer before the feed orifice? It may be plugged. The discharge pressures you have indicates no load and that is usually a sign of a restriction. Is there a liquid line drier. it may be plugged. |
Trade: Contractor employee,wholesale sales,contactor,sales
If you can still smell the burnout after a year then it was a bad burnout.
My guess would be that the wrong dryers were used.There are two dryers ,,,,,right??? My next guess would be a partially plugged system. Unless you can find something else you should revover the charge,replace the dryers with sporlan type HH dryers and refill will new freon.Hopefully you don't need a new compressor. No matter what you do,make sure you remove the orfice and clean it. |
| high head pressure low suction | tcbaker72 | Residential HVAC Forum | 51 | 09-28-2011 07:23 AM |
| Fluctuating Head Pressure | ravenirish | Residential HVAC Forum | 4 | 07-30-2011 12:27 AM |
| high head pressure low suction | whitelaker | General HVAC Discussion | 6 | 07-04-2011 08:16 AM |
| high head pressure | par2 | General HVAC Discussion | 4 | 06-29-2011 09:25 AM |
| new system with Aspen coil, low head pressure | Chuck78 | Residential HVAC Forum | 14 | 07-02-2009 09:42 PM |