Old 07-08-2009, 10:47 PM   #41
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 609
Default

Re: high head pressure low suction


Quote:
Originally Posted by mechanicalDvr View Post
I have worked on many of them but most had TXVs. I go back to the old tan GEs with the controls in the top shell with the linset coming out the very bottom. I am close to 50 and have been doing this stuff since I was a kid in a family run business, where if you could walk you could work. I got a loaded toolbox for Christmas at 5 yrs old.
I never doubt some of the ways systems used to be operated. Those old GE heat pumps, as well as some Rheem/Ruud heat pumps, had air pressure switch controlled defrost controls in them.

RoBoTeq is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. HVACSite.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 07-09-2009, 12:08 AM   #42
Semi electrician
 
mechanicalDvr's Avatar
 
Trade: HVAC tech
Join Date: Jun 2009
Location: New Jersey
Posts: 250
Default

Re: high head pressure low suction


Quote:
Originally Posted by RoBoTeq View Post
I never doubt some of the ways systems used to be operated. Those old GE heat pumps, as well as some Rheem/Ruud heat pumps, had air pressure switch controlled defrost controls in them.

Oh man that is a blast from the past.
mechanicalDvr is offline  
Old 07-09-2009, 11:36 PM   #43
Member
 
hvactech's Avatar
 
Trade: commercial/residential HVAC service/installation 20+years
Join Date: Jun 2009
Location: MI
Posts: 89
Send a message via AIM to hvactech Send a message via Yahoo to hvactech
Default

Re: high head pressure low suction


Wow, 3 pages and the original question was never really answered, Or was it? Where the hell is TC and did he get the answer he was looking for? I sure hope so after all that fuss!
hvactech is offline  
Old 07-10-2009, 09:28 AM   #44
Junior Member
 
bwalley's Avatar
 
Trade: Florida State Certified A/C Contractor CAC1816055
Join Date: Jul 2009
Location: Plant City, Florida
Posts: 15
Default

Re: high head pressure low suction


Quote:
Originally Posted by RoBoTeq View Post
What else does it do? Is it electrically operated? Thermally? Does it change the metering somehow?
No it is a mechanical (orifice) metering device in the cooling mode and when the unit is turned on in the heat pump mode, it allows the refrigereant to go around it, so it will not impeded the flow.

I will see if I can dig one up and take a picture of it.
bwalley is offline  
Old 07-10-2009, 10:48 PM   #45
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 609
Default

Re: high head pressure low suction


Quote:
Originally Posted by bwalley View Post
No it is a mechanical (orifice) metering device in the cooling mode and when the unit is turned on in the heat pump mode, it allows the refrigereant to go around it, so it will not impeded the flow.

I will see if I can dig one up and take a picture of it.
So it is a bypass only for a fixed orifice rather then for a TXV. That makes more sense. Must have been between fixed metering using cap tubes and sliding pistons that allow full bypass when slid in one direction.
RoBoTeq is offline  
Old 07-12-2009, 08:52 PM   #46
Junior Member
 
Peal's Avatar
 
Trade: Residential
Join Date: Jul 2009
Posts: 3
Default

Re: high head pressure low suction


I think bwalley is correct. 3 things will cause high head pressure; poor air flow across condenser, overcharge, or non condensable in system. Recover charge, check system for leaks, pull vacuum, and weigh in new charge.

Last edited by Peal; 07-12-2009 at 08:54 PM.
Peal is offline  
Old 07-12-2009, 11:40 PM   #47
Member
 
scooter's Avatar
 
Trade: Residential,light commericial hvac +
Join Date: Apr 2009
Location: Saginaw, MI.
Posts: 57
Default

Re: high head pressure low suction


too small a piston, too much airflow over evap coil, restriction in liquid line (filter/drier) condensor way below coil, condensor under a deck, condensor located in very hot envoiroment, there is alot more then three!
scooter is offline  
Old 07-13-2009, 07:31 PM   #48
Junior Member
 
Peal's Avatar
 
Trade: Residential
Join Date: Jul 2009
Posts: 3
Default

Re: high head pressure low suction


Scooter:
too small a piston, restriction in liquid line (filter/drier)

Ever put a unit into pump down. This is compete blockage of the liquid line. During pump down, no high discharge pressure. Besides if there is a partial restriction, the suction pressure will be low because the evaporator is being starved. Low suction pressure, low discharge pressure because of restriction. Unless overcharge, poor air flow across condenser, or non condensable in system.

scooter
condensor located in very hot envoiroment

Are you talking about the unit having a higher discharge head pressure on a hot day compared to a cooler day? Sure, on hotter days the discharge pressure will be higher. But this is not abnormally high head pressures. These are normal head pressures associated with hot days. If the pressures are higher then the normal hot day pressures, then it is because of poor air flow across condenser, overcharge, or non condensable in system.

Scooter:
condensor under a deck

Poor air flow across the condenser.

scooter:
too much airflow over evap coil

I agree that the discharge pressure will be higher, along with a higher suction pressure. But tcbaker72’s opening statement was, high head pressure low suction”
Peal is offline  
Old 07-14-2009, 10:35 PM   #49
Member
 
scooter's Avatar
 
Trade: Residential,light commericial hvac +
Join Date: Apr 2009
Location: Saginaw, MI.
Posts: 57
Default

Re: high head pressure low suction


TC is MIA
I am mearly trying to point out that all to often tunnel vision sets in and that there are no two systems that can be repaired with a cookie cutter repair.
you are obviously convinced that there are non-condensables in the system, great, good advice, my point is that there are never X number of answers in such a dynamic industry.
what if the furnace/air handler fan is quiting, due to a relay or open winding, what if the blower wheel is so filthy or has a shoping bag stuck in it that its capacity is 1/2 what it should be. Unless TC answers these questions and any more that you throw his way then we are all just peeing in the wind without being able to see the system first hand.
Sorry if I stuck a burr under your saddleblanket.
Scooter
scooter is offline  
Old 07-15-2009, 12:25 AM   #50
Junior Member
 
Peal's Avatar
 
Trade: Residential
Join Date: Jul 2009
Posts: 3
Default

Re: high head pressure low suction


Quote:
Originally Posted by scooter View Post
Sorry if I stuck a burr under your saddleblanket.
Scooter
If my replay was callused, I am sorry.
Quote:
Originally Posted by scooter View Post
what if the furnace/air handler fan is quiting, due to a relay or open winding, what if the blower wheel is so filthy or has a shoping bag stuck in it that its capacity is 1/2 what it should be.
Scooter
Scooter, this is what I think. If the evaporator fan is not running for whatever reason, or if the squirrel cage capacity is reduced, then the evaporator heat absorption would be reduced. All of the liquid refrigerant would not be evaporated. Some of the liquid refrigerant would be returning to the compressor. This would show up as low suction pressure, one of the diagnoses reported, but there also would be low superheat.

This is what tcbaker72 said:
Quote:
Originally Posted by tcbaker72 View Post
. the superheat never fell below 18 degrees.


You are correct; there should be more information to make a better judgment call, but based on what he reported, I will stick with non condensables for now.
Peal is offline  
Old 08-16-2011, 07:00 PM   #51
Junior Member
 
rico52177's Avatar
 
Trade: Air Conditioning/
Join Date: Aug 2011
Posts: 2
Default

Re: high head pressure low suction


Quote:
Originally Posted by tcbaker72 View Post
i am working on a trane condensor when I arrived at the job site I found the eveporator frozen solid. I thawed it out replaced the filters and cheked the coil it was fairly clean. I then found the pressure at around 45 psi on the suction and 185psi on the head. it was 90+ degrees out so I proceeded to add some refridgerant to the system and raised the head pressure to around 285 but could not get the suction above 50 psi. the superheat never fell below 18 degrees. I am thinking I have the wrong or missing piston or the compressor is not working properly. any ideas would help

If you add freon and the head pressure goes up but, not the suction...ou more than likely have a bad txv
rico52177 is offline  
Old 09-28-2011, 07:23 AM   #52
Junior Member
 
chrisfrost's Avatar
 
Trade: residential hvac repair and component upgrade
Join Date: Sep 2011
Posts: 4
Default

Re: high head pressure low suction


Also a semi-stuck reversing valve can restrict refr flow and to the previous poster that said that the refr is only metered in 1 direction would be a new 1 to me as I live and work in Phoenix where the heat pump is king and I've never seen a heat pump that was'nt metered both in cool and heat mode between evap and cond . Oops , I just noticed this is an old thread ,,,,,,

Last edited by chrisfrost; 09-28-2011 at 07:26 AM. Reason: noticed old post
chrisfrost is offline  
Old 08-05-2012, 09:03 PM   #53
Junior Member
 
Residentialtech's Avatar
 
Trade: Hvac
Join Date: Jul 2012
Posts: 11
Default

Re: high head pressure low suction


Sounds like the txv is bad
Residentialtech is offline  
Old 11-28-2012, 12:32 PM   #54
Junior Member
 
MajorNelson's Avatar
 
Trade: AC Contractor
Join Date: Nov 2012
Location: Florida
Posts: 1
Default

Re: high head pressure low suction


I have an AmerStd with an accumulator. Works well in cooling but head goes straight up in heat. Low suction and I assume non cons but was wondering about the sizes of the new condensing coils vs evaporate coils?
MajorNelson is offline  
Old 11-28-2012, 04:45 PM   #55
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 844
Default

Re: high head pressure low suction


Quote:
Originally Posted by MajorNelson View Post
I have an AmerStd with an accumulator. Works well in cooling but head goes straight up in heat. Low suction and I assume non cons but was wondering about the sizes of the new condensing coils vs evaporate coils?
Sounds like a restriction at/in the outdoor metering device.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Join Now... It's Fast and FREE!

I am a professional contractor
I am a DIY Homeowner
Drywall Talk is for
PROFESSIONAL CONTRACTORS ONLY!

At DrywallTalk.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?


SEO by vBSEO 3.6.1