HELP!: Heat Pump Heating not working
Old 10-10-2010, 01:28 AM   #1
paragon670's Avatar
Trade: HVAC Commercial/Residential EPA Univ Cert
I am diagnosing a heat pump. The customer said it worked great during the cooling season, but when she turned the thermostat to heating, the thermostat started smoking. I took off the cover to the thermostat, jumpered the red with yellow, ac worked great, then jumpered red with white, and started sparking alot so i couldnt keep it that way because i felt the transformer and it was getting very hot. Please help! Any ideas??
paragon670 is offline
Old 10-10-2010, 08:42 PM   #2
Techseabreeze
Techseabreeze's Avatar
Trade: Residential Heating and Cooling New Instalations and Repair
Re: HELP!: Heat Pump Heating not working
If your transformer became very hot it most likely took out the windings. Transformers should have a 3 amp. max. fuse inline with the Red wire just as it leaves transformer to prevent something like this from happening. Sounds to me you are needing to repair wiring, thermostat and replace the transformer. Better get some fuses and prevent the possibility again as you find the reason for thermostat shorting. Good Luck
Techseabreeze is offline
Old 10-12-2010, 12:39 PM   #3
if your trans is working fine between r and Y then it's not likely the transformer. if it was it would be doing that with r to g, r to y and r to w. it sound like there is a short in the W wire shorting the circuit to ground.
Old 10-13-2010, 01:25 PM   #4
cobia's Avatar
Trade: service tech/install
Is it a Rheem or Ruud heat pump? If you jump R and Y and got AC without energizing the reversing valve you will have to get 24v to your reversing valve for heating mode. A heat pump thermostat energizes Y on any initial call for cooling or heat. The W terminal is the second call for heat.
cobia is offline
Old 11-24-2010, 01:14 AM   #5
jclemmojoe's Avatar
Trade: Retired
I have a Dayton heat pump, made by Rheem/Ruud (I think) and have recently installed a new Tempstar touch screen programmable thermostat. The thermostat is rated 2 heat and one cooling. My primary heat source is oil forced air upflow furnace with the heat pump added later with a fossil fuel kit installed. The system has worked great with a Maple/Chase 9721 programmable thermostat for years but the clock portion of the screen lost several of the numbers so I had to replace it. Everything works fine except I can't get the reversing valve to switch to heating. When the stat calls for heat the furnace comes on. I have all the schematics, thermostat, fossil fuel kit and heat pump. What would you charge me to review the schematics and provide me a solution to my problem? I could Fax or mail copies to you. There is no rush, although I am spending more to heat the house than I need to.
Thanks,
Joe Clemmons
jclemmojoe is offline
Old 12-18-2010, 12:12 PM   #6
SERVICERMANMAN's Avatar
Trade: service man man man
Originally Posted by paragon670 View Post
i am diagnosing a heat pump. The customer said it worked great during the cooling season, but when she turned the thermostat to heating, the thermostat started smoking. I took off the cover to the thermostat, jumpered the red with yellow, ac worked great, then jumpered red with white, and started sparking alot so i couldnt keep it that way because i felt the transformer and it was getting very hot. Please help! Any ideas??
thats basice service work man go home
SERVICERMANMAN is offline
Old 12-18-2010, 05:54 PM   #7
costello's Avatar
Trade: heating,cooling,refrigeration
well if you did not take out transformer, If you are trying to get the heat pump to work and you get the ac to work in cooling mode by jumping r to y then you need to jump r,g,y,(o,b) connections. But it does sound like the short is on the w connection so the wire is either shorted or you have bad relay. Put a fuse in line and try again.
costello is offline
Old 02-09-2011, 01:44 PM   #8
fliks's Avatar
Trade: lisensed contractor
Take the thermostat wires off at the unit then check the white to ground. If you get continuity it is in the wire if not it is probably in the upstream wiring or controls. I have seen people install new t-stats and run a screw into the wires.
fliks is offline
Old 02-21-2011, 11:34 AM   #9
josuevos's Avatar
Trade: air conditioning heating plumbing
Red face
If in doubt ohm it out. Gotta be a bad white wire.
josuevos is offline
Old 02-21-2011, 11:38 AM   #10
josuevos's Avatar
Lightbulb
Thanks,
Joe Clemmons
R u sure you got the heat pump wired right. Sometimes u gotta have the blue wire instead of orange. Try heat when reversing valve is energized.
josuevos is offline
Old 12-21-2011, 02:18 PM   #11
WoodyH's Avatar
Trade: Furnace Repairs
Furnace Repairs
Similar clients have had this same issue, and the problem turned out to be the transformer.
WoodyH is offline
Old 12-21-2011, 08:06 PM   #12
Tony Pullen's Avatar
I can't comprehend that this is a transformer problem...truth of the matter is..this is troubleshooting 101. any real tech could diagnose this problem in less than 5 min with an ohm meter. After you change the transformer and it still won't work, then call a tech. (hint....aux heat relay coil or wire)
Tony Pullen is offline
Heat pump creative wiring? ApplianceTech9 HVAC Pictures 9 01-18-2012 06:18 PM
need help with heil heat pump elite Residential HVAC Forum 19 10-05-2010 04:23 PM
Heat Pump Defrost cmr_3168 Residential HVAC Forum 0 01-25-2010 10:00 AM
Heat Pump with Economizer NoTime General HVAC Discussion 3 01-23-2010 02:16 PM
heil heat pump 10 yrs old J. R . Smith General HVAC Discussion 1 06-17-2009 09:08 PM