Old 05-12-2010, 08:16 PM   #61
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 594
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by hvaclover View Post
I call your attention to Nordynes' ten year comp warranty. No requirement for an LLD on their R22 system.

Can't speak for their 410A systems but I am sure they probably do.

Even Lennox owned Aire Flo brand 410A system come with an LLD.
Are you saying that Nordyne does not require a LLD at all on the R22 system? Or are you saying that the LLD is factory installed in the outdoor unit?

When you say the Aire Flo units come with a LLD, are you saying there is a LLD factory installed in the units, or that there is a LLD laying in the box that needs to be installed in the liquid line?

RoBoTeq is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. HVACSite.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 05-12-2010, 08:20 PM   #62
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 594
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by beenthere View Post
If you have to ask how much moisture is in these driers. Then how can you size one correctly?

Not meant to be insulting, or offensive toward you in any way.

A filter drier rated to hold 400 drops of moisture. Can hold 20 grams. Its takes 28.35 grams to equal 1 ounce. So the above filter could hold .7 ounce(taking weight, not volume).

There are 16 ounces to the pound. A gallon of water weighs 8.33 pounds at 50°F. So that filter drier can only hold .0052 gallon of water/moisture.

The next factor that varies a filter driers ability to hold moisture. Is the refrigerants ability to absorb moisture(the moisture solubility of the refrigerant). As the refrigerant warms up, its solubility increases, and it will pull moisute from the filter.

Lucky, maybe, maybe not.

You may have seen the effects more often then you think, or know of.

That unexplained sticking/stuck piston at the evap. That clogged cap tube on heil/ICP heat pumps(and some other brands).
The clogged filter drier. Sticking rods in a TXV. A shorted compressor(even though there is no acid). the system with non condensables(some of that non condenseable is water vapor,).

There's more.
Darned good post! There are so many things that go on that too many techs don't consider because the systems keep on running, even if it is not under the best of conditions.
RoBoTeq is offline  
Old 05-12-2010, 11:50 PM   #63
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by beenthere View Post
Post a link to the specs that say that.
Sorry Been. You are going to have to do a little research. I attended a seminar by Sporlan and learned a hell of a lot about driers and other flow devices that most techs are very sketchy on.


Good hunting.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-12-2010, 11:54 PM   #64
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by RoBoTeq View Post
Are you saying that Nordyne does not require a LLD at all on the R22 system? Or are you saying that the LLD is factory installed in the outdoor unit?

When you say the Aire Flo units come with a LLD, are you saying there is a LLD factory installed in the units, or that there is a LLD laying in the box that needs to be installed in the liquid line?
On Nordyne R22 systems they do not SPECIFY a drier must be installed to qualify the ten year warranty.

Aire Flo 410A units ship LLDs loose and they must be field installed.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-13-2010, 12:20 AM   #65
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by hvaclover View Post
Sorry Been. You are going to have to do a little research. I attended a seminar by Sporlan and learned a hell of a lot about driers and other flow devices that most techs are very sketchy on.


Good hunting.

LOL...

So are you using those driers.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 05-13-2010, 12:48 AM   #66
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 594
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by hvaclover View Post
Sorry Been. You are going to have to do a little research. I attended a seminar by Sporlan and learned a hell of a lot about driers and other flow devices that most techs are very sketchy on.


Good hunting.
Oh hoooo! More of that "someone told me" stuff, eh?
RoBoTeq is offline  
Old 05-13-2010, 12:22 PM   #67
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by RoBoTeq View Post
Oh hoooo! More of that "someone told me" stuff, eh?

Gime a break, Robin? It's not like they hand out Cliff notes at the end of a seminar.

I have my notes I took during the seminar.

But I did find it on the web. So, happy hunting
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-14-2010, 07:02 PM   #68
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Sporlan doesn't use adsorbers in their filter driers.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 05-15-2010, 04:36 AM   #69
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by beenthere View Post
Sporlan doesn't use adsorbers in their filter driers.

You ain't diggin' very deep Been. Sporlan, Alco, they all have it.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-15-2010, 07:18 AM   #70
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by hvaclover View Post
You ain't diggin' very deep Been. Sporlan, Alco, they all have it.

I'm not digging at all.

If you know they make them. Post a link to that model liquid line/suction line filter drier. Or post the model number of the drier.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 05-15-2010, 12:21 PM   #71
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by beenthere View Post
I'm not digging at all.

If you know they make them. Post a link to that model liquid line/suction line filter drier. Or post the model number of the drier.
I stopped doing other folks leg work a long time ago.

You're welcome to believe or not.

I got nothing to gain either way.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-15-2010, 01:24 PM   #72
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 594
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by hvaclover View Post
I stopped doing other folks leg work a long time ago.

You're welcome to believe or not.

I got nothing to gain either way.
I came up with nothing either. Now it is just a matter of my time being wasted by an unsupported claim of someone else. What is to gain is integrity of your word.
RoBoTeq is offline  
Old 05-15-2010, 03:14 PM   #73
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Then I stand by my post. Unbrazing a filter drier will cause it to release moisture.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 05-15-2010, 08:18 PM   #74
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


good for you guys!

BTW i never endorsed reusing old filter driers.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-15-2010, 08:32 PM   #75
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


Look guys:
I took a lot of heat for using bone dry CO2 as a braze purge.

I threw up all kinds of data supporting my claim from a spec sheet that called for flowing CO2 copper lines for medical use to statements from Harris brazing and a hundred other references. All the while i was proving my point I was taking shots of the worst kind.

Even when i proved beyond a shadow of a doubt I am still taking guff for using CO.


For that reason I am not going to go dig up anything on this issue and take the chance of a bunch of yahoos giving me grief even after i have proven my point.

So believe if you like. Your life won't change either way but I at least won't get my character smeared again.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-15-2010, 08:56 PM   #76
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 594
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by hvaclover View Post
Look guys:
I took a lot of heat for using bone dry CO2 as a braze purge.

I threw up all kinds of data supporting my claim from a spec sheet that called for flowing CO2 copper lines for medical use to statements from Harris brazing and a hundred other references. All the while i was proving my point I was taking shots of the worst kind.

Even when i proved beyond a shadow of a doubt I am still taking guff for using CO.


For that reason I am not going to go dig up anything on this issue and take the chance of a bunch of yahoos giving me grief even after i have proven my point.

So believe if you like. Your life won't change either way but I at least won't get my character smeared again.
But smearing each other is the only thing keeping this site going.
RoBoTeq is offline  
Old 05-16-2010, 05:43 AM   #77
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by RoBoTeq View Post
But smearing each other is the only thing keeping this site going.

Robo u are one of the better people I know.
You could stomp on most fellas, but you don't.

RESPECT MY MAN I say to you.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-16-2010, 01:24 PM   #78
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 594
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by hvaclover View Post
Robo u are one of the better people I know.
You could stomp on most fellas, but you don't.

RESPECT MY MAN I say to you.
Thank you. I've been stomped on and I didn't like it.
RoBoTeq is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
FAU we installed in attic pcplumber HVAC Pictures 9 06-04-2011 05:53 PM

Join Now... It's Fast and FREE!

Privacy Badge
I am a professional contractor
I am a DIY Homeowner
HVACSite.com is for
PROFESSIONAL HVAC CONTRACTORS ONLY!

At HVACSite.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?


SEO by vBSEO 3.6.0