I'm with you on this one. Unfortunately, too many installs were being made without filter/driers installed and compressors were failing prematurely.
Heil started shipping driers about five years ago in all it's units above it entry level model.

All the 410A units are sue as shootin' coming with driers now.

__________________
Not Stupid, Just slow
hvaclover is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. HVACSite.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 05-09-2010, 04:24 PM   #42
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by carmon View Post
The drier shgould not be inside the condensing unit. I gueess there are to many problems with people not installing them,I sure wish they would just send it with the unit and let us install it ,oh wel lwishfull thinking.

If they just sent a drier with for the techs to install. Too many driers would end up sitting as stock on the service trucks.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 05-09-2010, 07:34 PM   #43
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 594
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by beenthere View Post
If they just sent a drier with for the techs to install. Too many driers would end up sitting as stock on the service trucks.
Or worse, tossed in the trash pile because they already have too many of them. This is what happened that caused the compressor manufacturer's to require equipment manufacturer's have filter/driers installed in the outdoor units in order to get the measly 20 month warranty that compressor manufacturer's give for compressors.
RoBoTeq is offline  
Old 05-09-2010, 07:49 PM   #44
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Not bad, for a product, they have little to no control over how its used.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 05-09-2010, 09:27 PM   #45
Old and Grumpy
 
John Markl's Avatar
 
Trade: Owner, Markl and Sons Cooling and Heating, Sherman, TX
Join Date: Mar 2010
Location: Sherman, Tx
Posts: 11
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by beenthere View Post
If they just sent a drier with for the techs to install. Too many driers would end up sitting as stock on the service trucks.
Why put them in with the unit they came with, when you can sell them out of your flat-rate book later?
John Markl is offline  
Old 05-10-2010, 05:10 AM   #46
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by beenthere View Post
If they just sent a drier with for the techs to install. Too many driers would end up sitting as stock on the service trucks.

Any tech who does that would get canned. Time used to be bad refer techs would get demoted to the ranks of resi hvac but at least these former refer tards still used a filter drier on ac installs no matter how bad their skill set in refer service used to be.

Now, years later, the trade crosses lines that once firmly seperated one another and we got a whole generation of low caste techs and mediocre indendant operators with no accountability.

It makes work for the compatent techs and independants, but at the cost the cost of bursing an already tattered industry reputation.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-10-2010, 08:21 AM   #47
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by John Markl View Post
Why put them in with the unit they came with, when you can sell them out of your flat-rate book later?
Unfortunately. Thats done/was done by more then one company.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 05-10-2010, 11:49 AM   #48
Energy mover
 
nicktech's Avatar
 
Trade: tech, instructor
Join Date: Jun 2009
Location: Union, NJ
Posts: 124
Default

Re: Factory installed LL dryer


tempstar sends all their condensers with a field installable sweat LLD. there great. they recommend them to be installed closest to the evap.
nicktech is offline  
Old 05-10-2010, 12:07 PM   #49
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 594
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by nicktech View Post
tempstar sends all their condensers with a field installable sweat LLD. there great. they recommend them to be installed closest to the evap.
Still? What brand of compressor is in them? What are the compressor warranties?
RoBoTeq is offline  
Old 05-11-2010, 08:55 AM   #50
Energy mover
 
nicktech's Avatar
 
Trade: tech, instructor
Join Date: Jun 2009
Location: Union, NJ
Posts: 124
Default

Re: Factory installed LL dryer


tempstar carries a copeland compressor with 10 yr warranty
nicktech is offline  
Old 05-11-2010, 04:25 PM   #51
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


seems the standard right now.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-12-2010, 12:15 AM   #52
Tech./Sales Consultant
 
RoBoTeq's Avatar
 
Trade: H-VAC Consulting
Join Date: Jun 2009
Location: Lancaster County, PA
Posts: 594
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by hvaclover View Post
seems the standard right now.
Not without an internally installed OEM filter/drier.
RoBoTeq is offline  
Old 05-12-2010, 04:48 AM   #53
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


I call your attention to Nordynes' ten year comp warranty. No requirement for an LLD on their R22 system.

Can't speak for their 410A systems but I am sure they probably do.

Even Lennox owned Aire Flo brand 410A system come with an LLD.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-12-2010, 09:23 AM   #54
Junior Member
 
carmon's Avatar
 
Trade: hvac contractor
Join Date: May 2010
Location: winnipeg
Posts: 18
Default

Re: Factory installed LL dryer


why would you put a liquid line drier near the evaporator coil,I have been in this trade for 30 years and have never on a/c work or refrigeration work put the drier near the evaporator,it just makes no sense to me. the manufactures must have a reason for it i suppose.
carmon is offline  
Old 05-12-2010, 09:33 AM   #55
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Because they can hold more moisture when they are in a cooler ambient temp. Then they can when they are in a hot ambient area.

At the evap coil. Doesn't apply to units with the evap coil installed in a non conditioned attic.

A LLFD can release moisture back into the system when it gets hot. If it is holding near its rated capacity at 75°F. At 95°F, it would have more moisture then it can hold/retain. And will release it back into the system.

Same reason that you should cut out the old filter drier, instead of unbrazing it.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 05-12-2010, 09:50 AM   #56
Junior Member
 
carmon's Avatar
 
Trade: hvac contractor
Join Date: May 2010
Location: winnipeg
Posts: 18
Default

Re: Factory installed LL dryer


I can see that but how much moisture are in these driers, If you size the drier correcrtly it will never fill with moisture,I have never had any trouble with driers releasing moisture,i imagine it happens ,i guess I Have just got lucky
carmon is offline  
Old 05-12-2010, 10:28 AM   #57
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by carmon View Post
I can see that but how much moisture are in these driers, If you size the drier correcrtly it will never fill with moisture,I have never had any trouble with driers releasing moisture,i imagine it happens ,i guess I Have just got lucky
If you have to ask how much moisture is in these driers. Then how can you size one correctly?

Not meant to be insulting, or offensive toward you in any way.

A filter drier rated to hold 400 drops of moisture. Can hold 20 grams. Its takes 28.35 grams to equal 1 ounce. So the above filter could hold .7 ounce(taking weight, not volume).

There are 16 ounces to the pound. A gallon of water weighs 8.33 pounds at 50°F. So that filter drier can only hold .0052 gallon of water/moisture.

The next factor that varies a filter driers ability to hold moisture. Is the refrigerants ability to absorb moisture(the moisture solubility of the refrigerant). As the refrigerant warms up, its solubility increases, and it will pull moisute from the filter.

Lucky, maybe, maybe not.

You may have seen the effects more often then you think, or know of.

That unexplained sticking/stuck piston at the evap. That clogged cap tube on heil/ICP heat pumps(and some other brands).
The clogged filter drier. Sticking rods in a TXV. A shorted compressor(even though there is no acid). the system with non condensables(some of that non condenseable is water vapor,).

There's more.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 05-12-2010, 10:41 AM   #58
Junior Member
 
carmon's Avatar
 
Trade: hvac contractor
Join Date: May 2010
Location: winnipeg
Posts: 18
Default

Re: Factory installed LL dryer


no problem I did not take it as insulting. I have never in my life many plug with contaminents ,if there is that much moisture present i will change out the drier more than once to take care of of it. I know now adays its getting worse with the new oils absorbing moisture,I just always install the drier at the condensing unit a/c or refrigeration
carmon is offline  
Old 05-12-2010, 05:10 PM   #59
Senior Member
 
hvaclover's Avatar
 
Join Date: May 2009
Location: burbs of detroit
Posts: 590
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by beenthere View Post
Because they can hold more moisture when they are in a cooler ambient temp. Then they can when they are in a hot ambient area.

At the evap coil. Doesn't apply to units with the evap coil installed in a non conditioned attic.

A LLFD can release moisture back into the system when it gets hot. If it is holding near its rated capacity at 75°F. At 95°F, it would have more moisture then it can hold/retain. And will release it back into the system.

Same reason that you should cut out the old filter drier, instead of unbrazing it.
That applied to driers that had ABSORBENT desiccant. Driers using ADSORBER types of desiccant will not give up moisture.
__________________
Not Stupid, Just slow
hvaclover is offline  
Old 05-12-2010, 06:29 PM   #60
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 568
Default

Re: Factory installed LL dryer


Quote:
Originally Posted by hvaclover View Post
That applied to driers that had ABSORBENT desiccant. Driers using ADSORBER types of desiccant will not give up moisture.
Post a link to the specs that say that.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
FAU we installed in attic pcplumber HVAC Pictures 9 06-04-2011 05:53 PM

Join Now... It's Fast and FREE!

Privacy Badge
I am a professional contractor
I am a DIY Homeowner
HVACSite.com is for
PROFESSIONAL HVAC CONTRACTORS ONLY!

At HVACSite.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?


SEO by vBSEO 3.6.0