Coleman 15.5 seer cooling problem R410
Old 07-22-2011, 01:45 PM   #1
tinman's Avatar
Trade: own HVAC company
This unit was only 1.5 years old. Customer cannot locate Installer. Unit has variable speed blower.
Had only 11* temp drop.., 77* D.B. return (67.4W.B.)..,66*D.B.supply at plenum.
58* low side 165psi..., 275psi hi side condenser temp 93* D.B.
Tryed using subcool chart on units sticker., i believe it wanted around 342-370 hi side P.S.I. at 95* ambient.,, started adding freon nothing happen,added more,nothing!
Got caught in the old trap.,,I'll lower that a-coil temp, must of let out 3lbs + freon! STILL 58* coil temp! hi side came down about 25lbs. Still had 11* temp drop inside home. I did have temp gauge on liquid line at cond.,believe it also stayed at 89*. Had a mind freeze and left!
tinman is offline
Old 07-23-2011, 10:05 AM   #2
Vaporx's Avatar
Re: Coleman 15.5 seer cooling problem R410
High suction and low head = bypass somewhere...either the reversing valve or compressor. If it's a heat pump, try switching the reversing valve a few times. If a scroll, try reversing the start and run leads at the contactor/capacitor to reverse rotation for a few seconds. If the compressor is hot, cool it down and see if that helps.
Vaporx is offline
Old 07-23-2011, 12:05 PM   #3
Suction and discharge seem real low for a 95 degree day.
Is the system exp valve? may not be feeding NG
Is their a strainer before the feed orifice? may be partially plugged.
I would think with 410A the suction should be double what you are getting around 118# S and the discharge should be around 418#D.
Old 07-24-2011, 06:05 PM   #4
Slight restriction in LLFD inside cabinet.
Old 07-25-2011, 08:52 AM   #5
Vaporx's Avatar
165 ain't low for the suction...
Vaporx is offline
Old 07-25-2011, 04:02 PM   #6
refermadness's Avatar
Whoa you can change the direction of a single phase compressor.?????
refermadness is offline
Old 07-25-2011, 05:22 PM   #7
Vaporx's Avatar
At least sometimes. The first time I did it was by mistake. But I had one scroll that seemed to be locked up. Did all the capacitor / hard start stuff with no success. Reversed the leads and it started running. Switched them back, and it ran normal. Go figure.
Vaporx is offline
Old 07-26-2011, 08:26 AM   #8
awesome You didn't have anything to lose and it worked so good job!!!!!!!
Old 07-26-2011, 10:27 AM   #9
The chart I am using shows the suction for air conditioning should be around 118# for 410A
Old 07-26-2011, 09:37 PM   #10
JohnH1's Avatar
As beenthere said
Restriction in the llfd. or the liquid line valve is partly closed Note your liquid line is cooler than outdoor temp. The dryor or valve is acting like a metering device.
JohnH1 is offline
Old 08-01-2011, 08:59 AM   #11
tinman's Avatar
Thanks Guys,have not been back to job site yet. Couple things on posts I may clarify.., at 15.5 seer it almost has to have x-valve..,it is not a heat pump..,I did not check to see If service valves were open.., I did not see nor do a LLFD temp in temp out test. Do not know if Coleman puts a strainer in there systems. Any more Ideas appreciated.., will keep every one posted!
tinman is offline
Sys not cooling well bagger Commercial HVAC Forum 22 08-06-2011 11:56 PM
Free home cooling idea - will this work? mperkel Residential HVAC Forum 2 07-13-2011 09:56 AM
Rental Cooling Towers cooling-tower Introductions 1 06-02-2011 01:16 AM
R22 to R410 conversion jpm136 Commercial HVAC Forum 6 08-08-2010 03:44 PM
Coleman Downflow Right side venting scubajj Residential HVAC Forum 5 02-02-2010 08:44 PM