Charging a heat pump - Residential HVAC Forum - HVACSite
Old 01-18-2012, 09:02 PM   #1
triple rectifier's Avatar
More specifically, the discharge superheat method; Ambient temp added to discharge temp. This method has served me well but doesn't work AT ALL in 410A systems. Anyone else use this method or know why that it doesn't jive with 410A?
triple rectifier is offline
Old 01-18-2012, 09:11 PM   #2
user
user2561's Avatar
Re: Charging a heat pump
In what mode of operation....
In heating the only way to be absolutely sure on a heat pump is to weigh the charge in.
user2561 is offline
Old 01-18-2012, 09:15 PM   #3
In heat pump mode...If it's a new install it's a no brainer. What I'm talking about is a unit you are not familiar with and need to get running.
Old 01-18-2012, 09:18 PM   #4
Just to clarify, I've installed heat pumps when the ambient is in the upper 30s/low 40s. When i know the factory charge and what needs to be added per 15' of lineset etc. But I've checked this method (discharge SH) and it's dead accurate with 22 systems...410A, not so much.
Old 01-18-2012, 09:25 PM   #5
user
user2561's Avatar
Right...same principle triple.
Use the calculators provided by the manufacturer for "ball park" but still manufacturer's require that system charge be weighed in on heat pumps during the heating season.
Keep in mind that R410,while it has minimum fractionation, it is still a zeotrope refrigerant which means it has more than one saturation temperature for each pressure. Those old methods once used with R22, a pure refrigerant, will not work the same with R410.
user2561 is offline
Old 01-18-2012, 09:33 PM   #6
Originally Posted by Cardinal View Post
Those old methods once used with R22, a azeotrope, will not work the same with R410.
Thanks for the reply. My 410 experience is limited. My tried and true methods of verifying charge (on HPs in HP weather) aren't adding up with the 410 splits. Roof tops, obviously, not an issue.
Old 01-18-2012, 09:46 PM   #7
user
user2561's Avatar
No worries mate....next time you're at the supply house pick up a newer PT chart that has the bubble and dew points for zeotropic blends.
user2561 is offline
Old 01-22-2012, 07:58 PM   #8
surenuff's Avatar
Trade: havcr
weight in charge in the heat pump mode per data plates, and then fine tune if needed. If around 60* you can artificially build heat in the condenser to simulate a 95* outside ambient temp and charge in the cooling mode with subcooling(if TXV) or evaporator superheat if fixed type orifice. Personally, I have not seen a problem between R22 or R410A The 410 fractionates so minutely that is is a trick to actually see any variation in the outdoor or indoor coil due to fractionation of the refrigerants.
surenuff is offline
Old 01-23-2012, 09:45 AM   #9
user
user2561's Avatar
Admittedly.....410a is classified as a "near" azeotrope refrigerant directly because there is little slide or glide between the blends but the fact remains that it can seperate. In fact there are many cases where it has which it turn will cause irractic pressures and operation of the equipment....this is why all zeotrope refrigerants, including 410, must be charged as a liquid.
410a, despite its good qualities, is a very poor refrigerant when compared to some others. Equipment components are more expensive due to a need for greater design & build to be able with stand the extreme differences. That being said 410 is here for now so we all have to deal with it.
Do not be surprised however to see 407c in the near future. It has a closer characteristics to R22 and a lower GWP than both R22 or R410.
user2561 is offline
Old 07-22-2013, 10:48 AM   #10
Acrepairexpertsmiami's Avatar
Trade: Hvac
yes I agree.. weigh in the charge for heating on a heat pump. simple as that.
Air Conditioning Repair in Miami FL
Miami Mechanical Contractors
"Everything HVAC/R"
Acrepairexpertsmiami is offline
Old 05-05-2014, 09:22 PM   #11
hvaclounge.com's Avatar
Trade: C-20
What is "heat pump mode"?
Come Visit HVAC Lounge to find great heating and air conditioning content.
hvaclounge.com is offline
Old 01-28-2015, 02:52 AM   #12
kevinlee's Avatar
Trade: Trade
Yes heat pump is very beneficial for home..its nice
kevinlee is offline
Old 06-12-2015, 01:34 AM   #13
Contractor Joe's Avatar
Trade: Construction Cleanup
410a, despite its good qualities, is a very poor refrigerant when compared to some others. Equipment components are more patio covers expensive due to a need for greater design & build to be able with stand the extreme differences. That being said 410 is here for now so we all have to deal with it.
Do you think there are going to be any significant changes in the upcoming build?
Contractor Joe is offline
Old 07-05-2015, 10:28 PM   #14
Bama's Avatar
Trade: hvacr
TXV? if so charge subcool manf spect if multiple stage disconnect y2 and charge in stage 1 only. superheat is fine if is piston metering device.
Bama is offline
charging, heat, pump
Heat pump creative wiring? ApplianceTech9 HVAC Pictures 11 01-09-2018 08:57 AM
Ruud Heat Pump gene2 General HVAC Discussion 9 08-09-2012 05:40 PM
need help with heil heat pump elite Residential HVAC Forum 19 10-05-2010 05:23 PM
Heat Pump Defrost cmr_3168 Residential HVAC Forum 0 01-25-2010 11:00 AM
Heat Pump with Economizer NoTime General HVAC Discussion 3 01-23-2010 03:16 PM