Trade: residentrial hvac contractor
Acid in York heatpump split system
What is the best way to treat acid in a hump pump system?
Re: Acid in York heatpump split system |
reclaim all the refrigerant, flush system with Rx-11 flush/nitro, install new liquid line and suction line dryers, use an acid neutralizer, pull a nice deep vacuum and use new refrigerant in the system.
ya what he said
Shoots Flaming Balls
Trade: tech
Sell them a new one
Re: Acid in York heatpump split systemI think you have "Sell them a new one on speed dail"
I would like to add to the mayhem by saying that since you will most likely have to cut several lines anyway to thoroughly flush the system and check valves, remove and tip the compressor to drain out the oil, or use a suction pump and dip tube to remove as much as possible. Measure and refill with fresh oil. Go have a beer!
Trade: commercial HVACR services
It depends on how much acid. How are you determining the acid exists. Secondly how did the acid get there? Hi temps over 300f plus and motor burns are the only acid causing things I know of in a sealed system. I'm sure there may be other things too but....
recovery and system purge are needed. An acid core filter drier should be installed preferably on the suction side, acid neutralyzer will help to carry acids to the drier. Replace the filter drier after 24 hrs and test again. Virtually all the oil in a system is carried through in just a few minutes of operation. Its allways best to replace the oil but not allways feasible. On a retest if acid still exists repeat as often as necessary. If real bad use flared filters or core driers for quick changes. Remove any suction driers after system is cleaned. ( do not use bi-flow type driers for this) Make sure the unit stays in cooling. |
#10 | |
Re: Acid in York heatpump split systemQuote:
use a suction line dryer to help trap and contain acids and debris from burnout in tandem with a liquid line dryer. a suction line dryer is equipped with 2 access ports, the pressure difference between the two corrolates to a restriction. the max allowable psi diff is 1psi max, any more means the filter is loaded and needs to be replaced. the acid causes the burnout, not vise versa! |
virtually all the oil stays in the compressors sump, or crankcase. only a small amount of oil that gets caught up in the low side suction is circulated in normal operation. if oil is being pumped out of the compressor sump than either a piping issue exists, refrig. migration to oil on off cycle and upon start up the pressure change causes the gas to volumize the oil into foam pushing it out, or there is an oil overcharge. since refrig oil is hygroscopic it will attract any moisture into it and this is where most of the acid resides. if a compressor burns out, your changing it anyway, if not pour the oil out or pump it out and replace a couple of times. then rx11 flush the sh*t out of the lines and most oil and contamination is removed. a new compressor will be filled with oil, if alot of old oil is in the system, it may return to the new compressor, over filling it and slugging it causing problems, not to mention it's most likely contaminated with the same acid that killed the original one.
Thanks
to the many of you that post I bought a flush kit about$90.00 back flush the line set and the condenser and flush the rx111 with freon added suction dryer which was hell in that tight space added bi flow liquid line dryer added acid away neutralizer to compressor suction port pressure chek w/ nitrogen pulled a deep vaccuum. Chek acid w/ litmus paper plastic gauge one week later everything: amp pressures super heat within limits Great to be talking to knowledgeable techs. I would buy you a beer if you were around. HEATME |
#13 | |
Trade: pipefitter
Trade: pipefitter
#15 | |
Trade: pipefitter
this is some dork from youtube!
this is what he tells the customer! what do you think? Quote:
#16 | |
Trade: pipefitter
i thought the only way a compressor could burn up is if you hit it with your torch!
![]() Quote:
Trade: pipefitter
i have not clicked on his video yet but I am SURE it is great!
![]() http://www.high-performance-hvac.com...enu-id-82.html |
Trade: Chiller engineer
It really does sicken me to think there are people out there who think they know everything about the principles of refrigeration.
I don't care what anybody tells you, there are only TWO things that are the root cause of compressor burn out on a hermetic or semi hermetic motor. 1. High suction temperatures 2. Moisture in the system Manufacturing defects are only responsible for less the 1/2 % of all compressor failures. Don't be fooled to think that moisture is the only cause for the formation of acid in a system. Excessively high temps result in the chemical decomposition of the refrigerant. When this happens, acid forms in the system and results in the burn out. A compressor burn out can be as a result of a more sinister problem so dont just clean the system up, replace the compressor and think the problem is solved. If you dont find out why the comp burned out, you can be sure you'll be back doing the job again! |
#19 |
I would ask from what source you got the stat that OEM failures are only 1/2%?
With the incredible number of different OEM comps in use today the quality is hardly uniform throughout the entire industry to allow your statement to be accurate.
#20 | |
Trade: pipefitter
i am trying to figure out if you are joking or kidding, or actually being serious???
high SUCTION temperatures????? so a 70 degree sst will destroy motor windings rated at 105 degrees celsius>?? what molecular component is it that breaks down and forms the acid from an hfc hydrflourocarbon refrigerant is it the hydrogen,florine or the carbon? obviously there would be no h20? Quote:
high superheat never killed a compressor! |
| new system with Aspen coil, low head pressure | Chuck78 | Residential HVAC Forum | 14 | 07-02-2009 10:42 PM |
| Low Evap Coil Saturation Temp on system | gene2 | Residential HVAC Forum | 8 | 06-22-2009 04:39 PM |