Anyone have experience with icm325 head pressure control. I heard it cant be used if system does not have a txv. Why would that be if we are just reducing condenser fan motor speed to maintain head pressure? Any input would be great!
sammy is offline   Reply With Quote
Join HVAC Site
Join the #1 HVAC Forum Today - It's Totally Free!
HVACSite.com - Are you a Professional HVAC Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for HVAC Contractors to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that HVACSite.com is a great community to join. Best of all it's totally free!
Join HVACSite.com - Click Here JOIN FOR FREE
Old 02-09-2010, 07:34 PM   #2
Higher head PSI = higher suction PSI This keep the evap from iceing up. I am not fermiler with the controll but I would assume that is the basics. Are you trying to operate durring cold weather?
JohnH1 is offline   Reply With Quote
Old 02-09-2010, 09:20 PM   #3
Default Icm325
It must operate at any outdoor temperature. I would say coldest being 15f.
Old 02-15-2010, 06:51 AM   #4
Because a TXv will close down as the evap gets colder. But a piston/fixed metering device system can and will over feed the evap while the ICM is keeping the pressure higher.
Then even after the ICM stops powering the condenser fan. The evap is flooded and will begin to frost over, and can feed liquid refrigerant back the the compressor.
Once most of the liquid is out of the evap. The condenser will begin to builds head pressure again, and start to over feed the evap again.
A TXV helps to prevent this from happening.
I do have several on piston systems that need to run when its 40° outside, and they work ok. If they run them when it below 40, they begin to frost up.
If your going to use them on piston systems. And these systems are for electronic rooms where humidity removal is not a problem. Increase your evap air flow to 450CFM per ton or more.
Of, just install a TXV.
PS: If your going to run them at 15° OD temp, install crank case heaters, if you want the compressors to last.