high head pressure low suction
Old 05-11-2011, 09:19 PM   #1
whitelaker's Avatar
I have a 3 ton system, 410a, running at 90 psi low side and 310 high side. When I arrived on site the indoor coil was frozen as well as the suction line on the line set. Checked the indoor coil (clean), air filter is new and I washed the outdoor condenser. The space temp was 83. I was thinking that the tx valve might be the problem...any thoughts
whitelaker is offline
Old 05-13-2011, 11:57 AM   #2
cascadehvac's Avatar
Trade: furnace and ac technician
Cool
Re: high head pressure low suction
looks like an air flow problem. are there vents closed? is the fan runnibg properly? if you leave off blower door does it run better?
cascadehvac is offline
Old 05-14-2011, 08:47 AM   #3
whitelaker's Avatar
I never thought to try that, I was too focused on a faulty tx valve when I go back I`ll give that a try, I`ll let you know
Old 05-17-2011, 08:12 PM   #4
JohnH1's Avatar
I would rather know the super heat and sub cooling along with inside temp and outside temp.
JohnH1 is offline
Old 06-04-2011, 05:25 PM   #5
josephsiaq's Avatar
Trade: Plumber, gasfitter, burner tech
FYI, if you techs carry a smart phone, windows phone or iPhone there is a great ac app called HVAC buddy. Plug in ALL of the info and out comes a diagnoses. Really helpful.
josephsiaq is offline
Old 07-03-2011, 06:38 AM   #6
Yep, pressures don't tell enough of what is happening to make a good diagnostic call.
Old 07-04-2011, 08:16 AM   #7
Vaporx's Avatar
"high head, low suction"
310 isn't high, unless the outdoor temp is 70F which probably isn't the case. Typical condensing temps for 13 SEER cooling equipment is 15-20 degrees above outdoor temp. The saturated temp for 310psi is right at 99F. So, if the OD was much above 85F, the head pressure was on the low side.
Superheat and subcooling measurements would tell you whether the problem is low air, low charge or TXV / LL restriction.
Vaporx is offline
high head pressure low suction tcbaker72 Residential HVAC Forum 51 09-28-2011 07:23 AM
High electric bill JohnH1 Off Topic 9 09-13-2011 10:56 AM
high efficiency for modular westernhvac Residential HVAC Forum 4 09-04-2009 08:45 PM
What brand of fuel oil pressure tester are you using? DuMass General HVAC Discussion 7 08-04-2009 07:27 AM
new system with Aspen coil, low head pressure Chuck78 Residential HVAC Forum 14 07-02-2009 09:42 PM