High head pressure fluctuating on a new 410a install - General HVAC Discussion - HVACSite
Old 06-02-2012, 02:03 PM   #1
popeyess's Avatar
I installed a new 410a complete system with new Orfice coil and new lineset. 70 degrees on install date and initial start up. Suction pressure was 110 and high side of 280. It ran for about 15 minutes. I added a little freon and the high side shot up to 425. I immediately thought I had a noncondensable stuck either at the filter drier or the metering device. Pumped the system down and checked, replaced drier and orfice. System does the same thing. The evaporator coil was a new Nordyne aluminum coil. I can't seem to figure out the problem. Any suggestions?<br>
popeyess is offline
Old 06-22-2012, 02:55 AM   #2
HVAC professional
moshei's Avatar
Re: High head pressure fluctuating on a new 410a install
Finding actual superheat or subcooling is easy . Simply hook it up to the system, let the system stabilize, and get your actual superheat or subcooling reading in real time. No charts, no calculations. Itís all done for you in the instrument.
moshei is offline
Old 06-25-2012, 12:46 PM   #3
dadsharem's Avatar
Trade: red seal refrigeration with a B gas ticket
if you thought it was noncondensibles why pump it down? you didn't say what happened to the suction pressure, and when you added some juice was it liquid?
dadsharem is offline
Old 06-25-2012, 07:09 PM   #4
VersaTek's Avatar
It's overcharged.
How much is a "little" that you added?
410 systems are precise, a couple of ounces can make the difference between...
110 / 280
and
130 / 320
a couple more ounces makes
140 / 475
VersaTek is offline
Old 06-26-2012, 05:44 AM   #5
On 70 degree days. I see a lot of R410A systems running at or around 110/280. So why did you add gas. Was the SC low, or the SH high?
Old 06-26-2012, 05:47 AM   #6
VersaTek's Avatar
I'm curious what the load on the evap was.
110 is just a tad low, but you are right, I see many running at that pressure (which I think is right around 32 degrees) if there is no load on the evap.
Fairly certain the unit is overcharged now.
VersaTek is offline
Old 06-26-2012, 05:52 AM   #7
R410a at 110 PSIG is 36 degrees saturation. Roughly equal to 63 PSIG with R22.
Good chance its over charged. Specially if that condense has a micro channel coil.
Old 06-26-2012, 06:53 AM   #8
VersaTek's Avatar
True.
I would have walked with it at 110 (without asking any questions) if it had a TXV.
Time for deminimus.
VersaTek is offline
Old 06-26-2012, 10:39 PM   #9
bowtech's Avatar
Set your superheat or sub-cooling and get it set it right. Then see what happens.
bowtech is offline
410a, fluctuating, head, high, pressure
high head pressure low suction tcbaker72 Residential HVAC Forum 54 11-28-2012 04:45 PM
Fluctuating Head Pressure ravenirish Residential HVAC Forum 4 07-30-2011 12:27 AM
high head pressure low suction whitelaker General HVAC Discussion 6 07-04-2011 08:16 AM
high head pressure par2 General HVAC Discussion 4 06-29-2011 09:25 AM
Trane R22 Heat Pump High head pressure heatme Residential HVAC Forum 4 05-18-2011 07:19 PM