high head pressure
Old 06-26-2011, 07:12 AM   #1
par2's Avatar
Trade: installer/service
high head pressure
i went to a carrier 410a split heat pump. The suction pressure was normal but the head would go up so high that it would trip the high pressure switch. The outdoor coil and fan are fine so i an leaning toward the txv. What other things should i be looking for?
par2 is offline
Old 06-26-2011, 02:20 PM   #2
Re: high head pressure
Restricted LLFD, and someone over charged it trying to get the vapor pressure up high enough.
Old 06-28-2011, 12:40 PM   #3
cascadehvac's Avatar
Trade: furnace and ac technician
are you running in heating or cooling?
cascadehvac is offline
Old 06-29-2011, 09:01 AM   #4
Vaporx's Avatar
And underfeeding TXV's are also a frequent problem these days.I don't see much Carrier stuff, but I'm guessing your system has one...lesser techs are overlooking them and adding Freon, trying to correct low suction/high superheat, as beenthere already noted.
You generally see 3 causes for high head: low condenser air, overcharge or significant non-condensibles...and I rarely see the non-condensibles. Low condenser air would still give you good suction and superheat numbers. If the subcooling is high and consistent from the condenser discharge to the evaporator TXV, that's likely the problem.
Vaporx is offline
Old 06-29-2011, 09:25 AM   #5
Vaporx's Avatar
Vaporx is offline
high head pressure low suction tcbaker72 Residential HVAC Forum 51 09-28-2011 07:23 AM
Fluctuating Head Pressure ravenirish Residential HVAC Forum 4 07-30-2011 12:27 AM
high head pressure low suction whitelaker General HVAC Discussion 6 07-04-2011 08:16 AM
Trane R22 Heat Pump High head pressure heatme Residential HVAC Forum 4 05-18-2011 07:19 PM
new system with Aspen coil, low head pressure Chuck78 Residential HVAC Forum 14 07-02-2009 09:42 PM