All the oil circulates through the system.
Most of the oil is in the sump at any one given time. But it all circulates through the system.
If it didn't. Then R410A could use mineral oil. The reason it can't use mineral oil. Is that it doesn't mix well with it. And won't be able to return the oil to the compressor.

If all the oil didn't circulate through the system. Then acid clean up by filters would be impossible. Since the filters require all the oil to pass through them to move the acid.

Next. Even if only the same 10 ozs of oil ever moved through the system. The oil that went through the filter drier would give up its moisture to the filter drier. Be returned to the compressor where it would absorb more moisture from the oil in the sump. Pass through the filter drier again. And give ups its moisture again. And repeat that process until the moisture was at a level lower then what it is, just from opening the oil container.

Now if you don't believe that.

Explain how an acid removal filter removes acid from the system.

Sporlan, and Parker(Sporlan now onwed by parker) have tech sheets on how oil circulates through the system. On how and why acid filters, and filter driers work.
I couldn't agree more and couldn't have put it better my self!

If we go back to the original statement that you can never remove moisture from POE by vaccing then I still have trouble agreeing with that.

On the grounds of that you could then go as far as saying that there is no point in pulling a vac on a system with POE as any moisture in the system will be absorbed by it and impossible to remove. (I do know we don't vac to only remove moisture, we vac to remove all the non-condensables too)

Not all systems use filter driers, just look at all the splits.....

TH3 M0L3 is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. HVACSite.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 01-18-2010, 03:22 PM   #22
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 857
Default

Re: micron gauge


When you install or have to open a system for service that uses POE oil.

You still want to remove as much moisture from the line set and coils as you can.
So vacuuming is still an important process, to minimize the moisture left in the system/line set, and or coils as much as possible.

What you don't remove. The POE will absorb. And the filter drier has that much more moisture it must remove.

Mini splits generally don't have room for a drier. So its probably a matter of lack of space then any other reason that they don't have driers.

Vacuuming removes moisture, nitrogen and CO2, and O2(combined, even without the moisture they're just air).

You would be surprised how much moisture isn't removed from mineral oil by vacuuming.

If you have the time, and curiosity.

Take a baby food jar. Drill a hole in the top. Insert a fitting that you can hook your vacuum pump to. And that can be sealed to the lid.
Then add 1 table spoon of water the the jar. And then add 4 times as refrigeration oil to the water, as you put in water(yes, 4 tablespoons).

Put the lid on. And if you have an electronic/digital scale, weight.
Then connect your vacuum pump to it. And run your pump as long as you have patience for. And yes, use your micron gauge. Look how long it takes to get a good vacuum(supposed good vacuum).

After 3 hours, you will still see water under the oil.



PS: No. The baby food jar will NOT implode from the vacuum. I wouldn't advise hitting it with something. But it was under a vacuum when it was bought with baby food in it.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 01-18-2010, 03:49 PM   #23
Junior Member
 
TH3 M0L3's Avatar
 
Trade: Chiller engineer
Join Date: Jan 2010
Posts: 11
Default

Re: micron gauge


Quote:
Originally Posted by beenthere View Post
When you install or have to open a system for service that uses POE oil.

You still want to remove as much moisture from the line set and coils as you can.
So vacuuming is still an important process, to minimize the moisture left in the system/line set, and or coils as much as possible.
I hope I never gave the wrong impression, I always perform a vacuum on any system I expose to the atmosphere.....always!

Quote:
Originally Posted by beenthere View Post
What you don't remove. The POE will absorb. And the filter drier has that much more moisture it must remove.

Mini splits generally don't have room for a drier. So its probably a matter of lack of space then any other reason that they don't have driers.
I think the reason they dont have driers is because it causes extra resistance on the refrigerant. If you use a drier, it will have a similar effect as either extending the pipe run, or adding extra bends in the pipework. For the splits to be more efficient, and have longer pipe runs, the driers are omitted....
I could be wrong though

Quote:
Originally Posted by beenthere View Post
Vacuuming removes moisture, nitrogen and CO2, and O2(combined, even without the moisture they're just air).
You are preaching to the converted

Quote:
Originally Posted by beenthere View Post
You would be surprised how much moisture isn't removed from mineral oil by vacuuming.
Yes, you are right. I would be surprised. But that, I guess, would depend on how much moisture is in the oil.
I can't imagine that amount of water in the system that it would form a layer under the oil, unless the oil was contaminated from the suppliers, or your vacuum pump failed during a vac and you did not have a check valve on your pump.....then it'd draw in loads of moisture....

Quote:
Originally Posted by beenthere View Post
If you have the time, and curiosity.

Take a baby food jar. Drill a hole in the top. Insert a fitting that you can hook your vacuum pump to. And that can be sealed to the lid.
Then add 1 table spoon of water the the jar. And then add 4 times as refrigeration oil to the water, as you put in water(yes, 4 tablespoons).

Put the lid on. And if you have an electronic/digital scale, weight.
Then connect your vacuum pump to it. And run your pump as long as you have patience for. And yes, use your micron gauge. Look how long it takes to get a good vacuum(supposed good vacuum).

After 3 hours, you will still see water under the oil.



PS: No. The baby food jar will NOT implode from the vacuum. I wouldn't advise hitting it with something. But it was under a vacuum when it was bought with baby food in it.
It's the time I lack. I know you will never pull a decent vacuum for as long as you have moisture present, and the jar wont make much of a mess if it did implode....
the pressure difference between the atmosphere and the jar would be less than 1 bar (about 14 psi) as it will be in some sort of vacuum.....another reason why using a vacuum to perform a system tightness test is highly inaccurate.....
TH3 M0L3 is offline  
Old 01-18-2010, 04:20 PM   #24
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 857
Default

Re: micron gauge


I use to take care of a bubble for a tennis court.

At 5"wc pressure in it. You couldn't open the handi cap emergency exit if you were in a wheel chair.
And if some one helped you open it. You were blown out the door with the chair and generally fell out of the chair.
The pressure had to be kept below 2"wc for that door to work right.

this bubble is 150' long and 40 foot high. And help up by only 1.75"wc under normal operating conditions.

So 14PSIG difference is a lot for many objects/containers.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 01-18-2010, 04:28 PM   #25
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 857
Default

Re: micron gauge


Test/experiment number 2.

Same jar. After cleaning and drying it out.
Place 5 drops of room temp water in it.
Connect vacuum pump and micron gauge.
Start pump and time it to see how long it takes to remove that water. It won't take long.

While you set up for the above mentioned experiment. Set a container with an ounce of water in it out side. And have it covered. You want the water in it to be the same temp as the outdoor air. Hopefully its 30F outside(it won't freeze sitting there while other test is going on).

After indoor test is done. Wipe out jar. Set it outside for 5 minutes(let it get as cold as it is outside). Then add 5 drops of water from the cold container you set outside earlier. Hook up your vacuum pump and micron gauge. And time how long it takes to remove the water. And the ice you just made.

At 20F. It takes rough;y 24 hours to remove 1 of moisture(1 refrigeration drop, is 1/20 of a gram).
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 04-18-2010, 06:59 PM   #26
Junior Member
 
westman's Avatar
 
Trade: Apartment maintenance
Join Date: Apr 2010
Posts: 1
Default

Re: micron gauge


Quote:
Originally Posted by Yuri View Post
It is ABSOLUTELY important that you have clean fresh oil in your vacuum pump or it will take forever to get a 500 micron vacuum. The moisture in the oil from the other jobs etc boils off and slows everything down.
Should you change the oil between every job?
westman is offline  
Old 04-19-2010, 05:30 AM   #27
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 857
Default

Re: micron gauge


Quote:
Originally Posted by westman View Post
Should you change the oil between every job?

Yes, you should.

If I'm doing only new line sets and evap coils. I don't change it between everyone.

Do one old line set, and or coil though. Change it. It makes a big difference in time.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  
Old 04-19-2010, 04:11 PM   #28
Junior Member
 
earl964's Avatar
 
Trade: Hvac service tech.
Join Date: Apr 2010
Posts: 2
Default

Re: micron gauge


If we don't use one we are told to pack up our stuff and go work some place else. New refrigerant cost way to much.
earl964 is offline  
Old 05-23-2010, 08:48 PM   #29
Junior Member
 
Mr freeze's Avatar
 
Trade: Lead refrigeration supervisor
Join Date: May 2010
Posts: 1
Default

Re: micron gauge


When doing refrigeration work you suppose to use micron gauge, I use every time you dont know how far down , I do cascade from -120f to -255f system.You have to pull these system down to 100 Micron it might take 2 day with two vacuum pump running and heat lamps. This is other way that the system is tight on leak when you have the micron gauge on the system. Pluse refrigerant is cost pre pound is high on these system 6 pound cost is 2,000 and up.Refrigerant pre pound cost for now days All my guys have their micron gauge and they all use them from system that run 1/2 pound to 600 pounds.

Last edited by Mr freeze; 05-23-2010 at 08:56 PM.
Mr freeze is offline  
Old 08-01-2010, 02:25 PM   #30
Junior Member
 
Rusty999's Avatar
 
Trade: Master HVAC Technician
Join Date: Jul 2010
Posts: 6
Default

Re: micron gauge


Great post on the use of micron gauges. Also I love the different viewpoints. Good point about the standing vacuum test. Here how I learned it: Pull system down to 1000 microns, then break vacuum with dry N2. Do this 3 times (triple evac). Pull down to 400 and allow too sit 45 min. If the reading climbs, then holds ( ex to 1500-2000) it's moisture. If it continues a slow climb without stopping, it's a leaker.

My understanding about mini splits is that a LLD isnt used because technically there's no liqid line outside the unit (types may vary). Both lines are low pressure, thats why theres no svc fitting on the second line. The metering device is in the condenser outlet like alot of general motors cars, so what you would think would be the liquid line has refrigerant flashing inside, which I guess would make it part of the evap circuit.
Rusty999 is offline  
Old 08-03-2010, 03:06 PM   #31
Junior Member
 
joeyd's Avatar
 
Trade: manufacturer
Join Date: Aug 2010
Posts: 1
Default

Re: micron gauge


I design and manufacture electronic service tools for the HVAC/R industry. I will soon be going to market with a new micron gauge, and I am looking for a few experienced service professionals who would like to participate in the evaluation of this new product. Preferably, a candidate would be one who uses micron gauges on a daily basis, has used a number of different products, would be willing to test my product over a number of weeks (preferably in conjunction with their own favorite gauge), and finally, provide an objective evaluation as to its overall performance and usefulness. In exchange for this effort, he/she will be given a gauge from the first production run at no charge, regardless of the favorable/unfavorable nature of the evaluation.

If you wish to be considered, please send me a private message, and I can provide more details.

Thanks,

JoeyD
joeyd is offline  
Old 09-17-2010, 03:38 PM   #32
Junior Member
 
Air Medic's Avatar
 
Trade: Tech
Join Date: Sep 2010
Posts: 3
Default

Re: micron gauge


Quote:
Originally Posted by earl964 View Post
If we don't use one we are told to pack up our stuff and go work some place else. New refrigerant cost way to much.
I'm with Earl. Refrigerant is way to expensive for this kind of money wasting.
__________________
Knoxville Air Conditioning Services
Air Medic is offline  
Old 09-27-2010, 11:49 AM   #33
Junior Member
 
HVAC Joe's Avatar
 
Trade: HVAC installer
Join Date: Sep 2010
Posts: 5
Cool

Re: micron gauge


Quote:
Originally Posted by sanpyon View Post
vacuum gauge very important, especially on low-temp system and you have to keep your oil in good condition all the time.
This sums it up. 'Nuf said.

_______________

Plumbing Boston is my life's work . . .
avoiding Jersey, where my wives lurk.

Last edited by HVAC Joe; 11-07-2010 at 04:38 PM. Reason: grammar and smiley
HVAC Joe is offline  
Old 01-23-2011, 09:05 AM   #34
Junior Member
 
HintonAC-LeoTav2's Avatar
 
Trade: Heating and Air Conditioning Service and Installation Tech
Join Date: Jan 2011
Location: Chalmette, LA
Posts: 5
Default

Re: micron gauge


What kind of micron gauges are you guys using? I was using a Fieldpiece SVG2 for about a year now and it is already crapping out on me (it reads 1880 microns when open to the atmosphere). I need something durable and worth the money. Fieldpiece makes a great Electric meter and amprobe however their vacuum gauge and superheat/subcooling meters are not up to par even if you baby them.
HintonAC-LeoTav2 is offline  
Old 02-14-2011, 12:07 AM   #35
Junior Member
 
nimnux's Avatar
 
Trade: HVAC
Join Date: Feb 2011
Posts: 1
Default

Re: micron gauge


digital gauges are more accurate and also expensive
__________________
Mr. Heat Mechanical Inc.
nimnux is offline  
Old 01-22-2012, 12:16 AM   #36
Junior Member
 
rlynch33's Avatar
 
Trade: HVACR COMMERCIAL SERVICE TECH
Join Date: Jul 2009
Posts: 1
Cool

Re: micron gauge


Quote:
Originally Posted by evapman View Post
how many guys use them? I'm a believer in them, allot of guys around here just use their gauges and let the vac pump run fo a hour or so and call it good, and get away with it. How they know the system is evaced. I don't know, have seen it take an hour to 3 hours to get down to 400 microns.
i use mine to verify for leaks when i"m done with any repair ETC.. Professionals use them.
rlynch33 is offline  
Old 04-03-2012, 01:07 AM   #37
Junior Member
 
combs custom cooling's Avatar
 
Trade: c20
Join Date: Feb 2012
Posts: 3
Default

Re: micron gauge


I used to use my sman3 and my JB micron gauge every time. now that I have a testo 557 I use it and the JB. I do this because i noticed that sometime the micron meters get stuck in a vacuum even when exposed to atmospheric pressure. I think its worth it though for the customer and of course I pride myself on having a low rate of call backs.
combs custom cooling is offline  
Old 04-20-2012, 09:22 PM   #38
Junior Member
 
chuckcrj's Avatar
 
Trade: HVAC/R Technician
Join Date: Nov 2010
Location: WI
Posts: 8
Default

Re: micron gauge


As for which micron gauge is the best, the Bluvac hands down.

With the leak rate indicator you can tell exactly what is happening inside the system.

It is very sensitive and will reveal any leaks in your vacuum setup.

It is the one JoeyD talked about in his post above, from Aug, 2010.

Last edited by chuckcrj; 04-20-2012 at 09:29 PM.
chuckcrj is offline  
Old 08-08-2012, 08:09 AM   #39
i am that guy
 
acefurnacefixer's Avatar
 
Trade: Service man
Join Date: Jun 2009
Location: NW Ohio
Posts: 32
Default

Re: micron gauge


Quote:
Originally Posted by DuMass View Post
I'm wondering how you can really work without a Micron gauge, especially these days with refrigerants that can fractionate when leaks occur and the sponge like moisture absorbing qualities of POE and even PAG if you do automotive AC. You really need to know that the system is dry and tight.
you cant and should not even attempt to put in a A/C system with out using a micron gauge.I use one every time I install or repair the pipeing side of a system. if i dont achive 50 microns, then i am not sure that my joints are tight. Your manifold is for charging a system......not to tell you if you have a tight system......thats the job of the micron gauge.
__________________
You can pay me now, or you can pay me later....but eventually you will pay me....
acefurnacefixer is offline  
Old 08-08-2012, 09:37 PM   #40
Senior Member
 
beenthere's Avatar
 
Trade: Service/Installation
Join Date: May 2009
Posts: 857
Default

Re: micron gauge


Quote:
Originally Posted by acefurnacefixer View Post
you cant and should not even attempt to put in a A/C system with out using a micron gauge.I use one every time I install or repair the pipeing side of a system. if i dont achive 50 microns, then i am not sure that my joints are tight. Your manifold is for charging a system......not to tell you if you have a tight system......thats the job of the micron gauge.
50 microns? A lot lower then needed.
__________________
How many times must one fix something before it is fixed?
beenthere is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Join Now... It's Fast and FREE!

I am a professional contractor
I am a DIY Homeowner
Drywall Talk is for
PROFESSIONAL CONTRACTORS ONLY!

At DrywallTalk.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?


SEO by vBSEO 3.6.1